Estimate for Generator Gas Line.

Recommended Posts

Errrrrrr, 3 pages and no takers? Estimates?[emoji16]


Sent from my iPhone using Tapatalk Pro
Your on the other side of the Raritan I believe. If so I don't venture into North Jersey, but if trench was dug we would provide and install pipe for around $1,000. Material is expensive because of the elbows they run $100 each. Hope that helps with your estimate search.

Glad I'm not the only one who finds him senseless and annoying. Just add to block list.

Sent from my XT1585 using Tapatalk

  • Like 1

Share this post


Link to post
Share on other sites

The gas line is not below ground though. It could be ran on basement ceiling then onto wall and out the side with a quick disconnect or cap couldn’t it?


Sent from my iPhone using Tapatalk Pro

Share this post


Link to post
Share on other sites

Yes you could. So your meter is in the basement? If so you cut existing pipe at meter, increase pipe out of meter to appropriate size, install say 1 1/4" x 3/4" tee (assuming existing is 3/4") tie existing back into new tee, continue 1 1/4" line to generator. Labor is more but material is less. Assuming unfinished basement and hanging pipe at bottom of joists it could still be done for $1,000. If finished basement or drilling joists it would be more.

 

Alright who deleted the best and most deserved statement I've seen yet? Unless bhunted asked for it to be removed Mod really should put it back. I would have screen shot it if I thought the censors were going to remove it.

 

Sent from my XT1585 using Tapatalk

 

 

 

 

 

 

 

 

 

 

 

 

  • Like 1

Share this post


Link to post
Share on other sites
2 hours ago, bhunted said:

The gas line is not below ground though. It could be ran on basement ceiling then onto wall and out the side with a quick disconnect or cap couldn’t it?


Sent from my iPhone using Tapatalk Pro

thats exactly what i did. was fortunate to already have a capped 3/4" T from an abandoned hot water heater that made it easy. I connected a shutoff there and allowed me to take my time running the line outside thru base ment/crawlspace-pia lol. Used stock off the shelf black pipe from home depot-cheap. i put a q/d on a brass coupling on the end where it is exposed to the weather but still covered it with a improvised grey plastic electric box. i put on a pressure gauge w a schraeder valve to pump in air for the pressure test then fitted the q/d. easy and inexpensive. shit. the 10' 3/4 flex ng hose with the fittings was the most expensive piece after the gen!  In fact when I went for the permit app no one had ever tried(legally) to hook up a portable gen like this and they had to invent some pprwrk, including a waiver that I would only operate it at least 10' (thus the hose) from the house/combustables.

  • Like 1

Share this post


Link to post
Share on other sites
3 hours ago, capt14k said:

Yes you could. So your meter is in the basement? If so you cut existing pipe at meter, increase pipe out of meter to appropriate size, install say 1 1/4" x 3/4" tee (assuming existing is 3/4") tie existing back into new tee, continue 1 1/4" line to generator. Labor is more but material is less. Assuming unfinished basement and hanging pipe at bottom of joists it could still be done for $1,000. If finished basement or drilling joists it would be more.

 

Alright who deleted the best and most deserved statement I've seen yet? Unless bhunted asked for it to be removed Mod really should put it back. I would have screen shot it if I thought the censors were going to remove it.

 

Sent from my XT1585 using Tapatalk

 

 

 

 

 

 

 

 

 

 

 

 

Yep, unfinished and attached to joists. Closest tap is to the dryer. Might even be the right size pipe. I have to look.

US Carb will make any custom length flexi gas line with coupling. So may only need 10' of solid gas line to get it outside.

Share this post


Link to post
Share on other sites
1 hour ago, siderman said:

thats exactly what i did. was fortunate to already have a capped 3/4" T from an abandoned hot water heater that made it easy. I connected a shutoff there and allowed me to take my time running the line outside thru base ment/crawlspace-pia lol. Used stock off the shelf black pipe from home depot-cheap. i put a q/d on a brass coupling on the end where it is exposed to the weather but still covered it with a improvised grey plastic electric box. i put on a pressure gauge w a schraeder valve to pump in air for the pressure test then fitted the q/d. easy and inexpensive. shit. the 10' 3/4 flex ng hose with the fittings was the most expensive piece after the gen!  In fact when I went for the permit app no one had ever tried(legally) to hook up a portable gen like this and they had to invent some pprwrk, including a waiver that I would only operate it at least 10' (thus the hose) from the house/combustables.

Yes, the rules the gen has to be a certain distance from house. Mine is about 20' from the house. All I have to do is roll it out of the shelter and plug everything in. Hmmm, I can prob do most of this. The crawling around on my bad knees is the worse part.

Share this post


Link to post
Share on other sites
13 minutes ago, bhunted said:

Yes, the rules the gen has to be a certain distance from house. Mine is about 20' from the house. All I have to do is roll it out of the shelter and plug everything in. Hmmm, I can prob do most of this. The crawling around on my bad knees is the worse part.

Two words...

Knee pads 

You can do this!

Share this post


Link to post
Share on other sites
Two words...
Knee pads 
You can do this!

Lmao! Hey, I don’t swing that way. [emoji23]
But seriously. I got a good set. Wore them once and was in heaven. Sad part is I forget I have them and bitch about it after I screw my knees up.

I spent 3 months working on the ground building a zen type garden for my wife and totally forgot about the effing pads. Crippled the hell out of me for 3 months afterwards and still hurting. Doc yelled at me big time! Got to remember getting old sux!
466a4b8ac9036e2de82f946677fd01e5.jpg



Sent from my iPhone using Tapatalk Pro

Share this post


Link to post
Share on other sites
Yep, unfinished and attached to joists. Closest tap is to the dryer. Might even be the right size pipe. I have to look.

US Carb will make any custom length flexi gas line with coupling. So may only need 10' of solid gas line to get it outside.

 

Of course you can tap off the dryer but you shouldnt. If you do you will likey have to increase all the gas pipe. Plus that is likely a 1/2" line. You basically need to run a homerun back to the meter in most likely 1" gas pipe and if you don't have 1" coming out of the house side of the meter you need to increase it to 1" at least until the first tee that goes to the generator and the rest of the house. You may have to run 1 1/4" you have to add up the total pipe distance from meter to generator then go to chart for generator and bbq. Rent, buy, or borrow a hand threaded and cut and thread in place.

 

 

Sent from my iPad using Tapatalk

  • Like 1

Share this post


Link to post
Share on other sites

I’m going to make a map of my layout and mark the length and size of each line coming out of the meter. Seems the only right way to hash this out. Then I’ll post it as a graphic here. Maybe it will also help with estimates. Got 3 projects going on here and I’m going nutso. [emoji57]


Sent from my iPad using Tapatalk Pro

Share this post


Link to post
Share on other sites
I’m going to make a map of my layout and mark the length and size of each line coming out of the meter. Seems the only right way to hash this out. Then I’ll post it as a graphic here. Maybe it will also help with estimates. Got 3 projects going on here and I’m going nutso. [emoji57]


Sent from my iPad using Tapatalk Pro
That will work. Post as jpg I can then mark it up with photo editor.

Sent from my XT1585 using Tapatalk

  • Like 1

Share this post


Link to post
Share on other sites

Whelp, did a rough sketch. When I get to my desk in the morning, I’ll do a more legible graphic.
So far all lines feeding something is only 1”....the line into the meter looks to be 1.5”.....



Sent from my iPad using Tapatalk Pro

Share this post


Link to post
Share on other sites

y'all are reminding me I need to install my conversion kit, and find a flexible gas line to run from the fitting in the garage.  question is can I run a hose that long. if I go to full length of my generator cable, we're talking at least 50' of hose.

Share this post


Link to post
Share on other sites
y'all are reminding me I need to install my conversion kit, and find a flexible gas line to run from the fitting in the garage.  question is can I run a hose that long. if I go to full length of my generator cable, we're talking at least 50' of hose.

You need to call the converter folks.


Sent from my iPhone using Tapatalk Pro

Share this post


Link to post
Share on other sites
On 9/20/2017 at 7:27 PM, capt14k said:

That will work. Post as jpg I can then mark it up with photo editor.

Sent from my XT1585 using Tapatalk
 

OK, hope this helps.... It's rough, but hopefully legible...

 

bhunted_gasline.jpg

Share this post


Link to post
Share on other sites

What is your total BTU? I estimate 385,000 which means you should increase the gas pipe to 1 1/2" from the meter to the furnace then if everything is 1" after that simply tap the 1" and continue that to the generator

 

Sent from my XT1585 using Tapatalk

 

 

 

 

Share this post


Link to post
Share on other sites
1 hour ago, capt14k said:

What is your total BTU? I estimate 385,000 which means you should increase the gas pipe to 1 1/2" from the meter to the furnace then if everything is 1" after that simply tap the 1" and continue that to the generator

 

Sent from my XT1585 using Tapatalk

 

 

 

 

Doesn't sound bad.... I have to go get that. Was late last night and forgot to get the btu.... I'm guessing about 275,000. At what point can I leave the lines alone or????

Share this post


Link to post
Share on other sites

You have to have minimum 1 1/4" to furnace or homerun from meter to generator up to 315,000.

 

275,000 sounds low. Usually it's 120 Furnace, 60 range, 45 dryer, and 40 water heater. Then your adding probably 120 for generator. I estimated low at 365,000.

 

Sent from my XT1585 using Tapatalk

 

 

 

 

Share this post


Link to post
Share on other sites
If all these devices won’t be used during a crisis, is there still a need? Like just the stove, furnace and water heater?

 

 

Sent from my iPad using Tapatalk Pro

 

 

No but if you want to be to code it should be done. Just the generator alone needs 1". If you are using furnace and generator it needs 1 1/4" to furnace

 

Sent from my XT1585 using Tapatalk

 

 

 

Share this post


Link to post
Share on other sites

Ok, so basically get a 1.5” to the furnace from meter and I can tap a 1” off that dead line out to the gen area with 1”. Did I get that right?


Sent from my iPad using Tapatalk Pro

Share this post


Link to post
Share on other sites

So, my meter is so damn old all the stickers have faded and fallen off. :)

What I could read from the hard stamped plaque has a box labeled "CFH" with a value of "275" in it.

The line after the meter into the house is 1" for about 14' linear.
1/2" tee for the water heater at 6'
3/4" tee for the furnace at 12' (that necks down to 1/2" after the shut off valve)
neck down to 3/4" at 14'
3/4" tee at 16', with the straight heading for the gas dryer.
3/4" pipe is the rest of the run out to the other side, with a 3/4" tee to the stove at 46'.
the 3/4" shutoff valve for future hookup to the generator is at about 60' distance.

I could probably replace a good chunk of the 3/4" line to the generator outlet if needed. It's all accessible and i'm not adverse to working with black pipe.  The question is, how does the size changes effect the final BTU number at the end of the run?

Share this post


Link to post
Share on other sites

Ummm, that meter and regulator should be replaced. I’m surprised your gas company didn’t insist on it. PSEG tells me when to replace it. The just replaced my meter, regulator and vent for free. This is the 3rd time over the decades I can recall them doing so. I’d give them a call if I were you.


Sent from my iPad using Tapatalk Pro

Share this post


Link to post
Share on other sites
PSE&G around here gives fewer shits than JCP&L does.  so few in fact it might actually be a negative number.
I've been here 16 years and this meter looks like it's original to the house (1986.)

Request it changed then. Should be no charge. Better to be safe than sorry.


Sent from my iPhone using Tapatalk Pro

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...

  • Recently Browsing   0 members

    No registered users viewing this page.



  • olight.jpg

    Use Promo Code "NJGF10" for 10% Off Regular Items

  • Supporting Vendors

  • Latest Topics

  • Posts

    • I very seriously doubt this has anything to do with terrorism.    1) Harbor pilots are VERY seriously vetted, and highly trained. Not to mention extremely well paid. My experience knowing a few of them, and knowing how they are recruited and screened tells me that there is a slim to highly unlikely chance that a harbor pilot would have participated in anything like that.    2) Maintenance of foreign flag ships is well known to be dubious. Especially these days. These were NOT US flag, Jones act sailors. It was (to my understanding) a largely Indian crew on that ship, with a Ukrainian Captain. Indian crews are not exactly known for being stellar.    3) The bunkers (fuel) these ships use is ‘Bunker C’, which is a heavy, dirty fuel oil that can, and usually is, pretty contaminated. This stuff ain’t your car grade gasoline or diesel fuel. It’s nasty.   It requires nearly constant filter changes and maintenance to the engine/generators. The ship took on fuel prior to departing port, which would stir up all kinds of shit in the fuel tanks, which would contribute to particulates in the fuel lines/filters.    4) I’d say the posting of the chief engineer for Maserek above was pretty spot on as far as chain of events.    This was a shitty accident, with horrible timing and outcome. Not a terror attack. 
    • I saw Lara's interview on Bannon's War Room, and that gave me pause for thought. Her conjecture depends primarily on the veracity of her sources. Regardless, if it's not applicable in any way to this ship disaster, the methods described seem valid to me. And worthy of consideration for the future. As I said before, IMO something is coming. Death by a thousand cuts? Lara Logan Provides Comprehensive Baltimore Update: Experts in Behavioral Analytics, Counter-Terrorism, and National Security Analyze Recent Incident | The Gateway Pundit | by Jim Hᴏft
    • Another big windfall for governments'. The 'winner'? Not so much. Mega Millions $1.13 billion winner is facing mega tax bill. The amount is staggering. - nj.com
×
×
  • Create New...